Brace Wall Panels & Alternate Brace Wall Panels.

Discussion in 'AutoCAD' started by Scott Townsend, Mar 12, 2005.

  1. The Feedback I received on some plans has the following comments:

    Identify all Brace Wall Panels @ min 4' and Alternate Brace Wall Panels less
    then 4'
    min 2'8" w/ hold downs min 1800 psf capacity shall be located within 8" of
    each corner.

    BWP/ABWP - min 3/8" ply w/28 @ 6" O/C edge 12" O/C Field


    I think I have an Idea of what they mean but not sure.

    So I just label BWP if there is a wall @ a corner that is 4' or more and
    ABWP if the wall from the corner is less the 4'

    More or less depending on placement of window/door, etc?

    Is this correct?

    Thanks,
    Scott<-
     
    Scott Townsend, Mar 12, 2005
    #1
  2. Scott Townsend

    Paul Turvill Guest

    Your interpretation is essentially correct. You will also have to call out
    the proper holdowns at the ABWP locations.

    Take a look at the Code Book in effect for your local jurisdiction. I can't
    believe you'd be submitting plans for approval without having that reference
    at your fingertips.
    ___
     
    Paul Turvill, Mar 12, 2005
    #2
  3. I like to Live Dangerously (-;

    I have the Residential Construction Code book put out by our County, though
    its not really laid out in any reasonable fashion. No Index or anything.

    The closest thing I found was a Softwall Brace Detail.

    So the Hold downs are the Simpson PHD2, HD8A and HT22 that I want connected
    to a Post or Double Stud?

    I'm guessing I'd use one on each wall coming from the Corner and at the Next
    Opening for Window/door?

    Thanks for your Help!
    Scott<-
     
    Scott Townsend, Mar 12, 2005
    #3
  4. Scott Townsend

    Paul Turvill Guest

    You should be able to find everything you need to know in the section of
    your code dealing with Lateral Design (wind and/or seismic). Sorry, but
    other than that, a public AutoCAD newsgroup just isn't an appropriate place
    for instruction in the details of building design, especially since code
    requirements and interpretations vary with jurisdiction. The references you
    mention sound like they're from the 1997 UBC, which has been superceded in
    many jurisdictions. However, I'm sure if you ask, your local Building
    Official will be happy to cite the exact Code section and paragraph for you
    to study. The Simpson catalog will also give you a variety of solutions,
    once you know what capacity holdowns you need.
    ___
     
    Paul Turvill, Mar 13, 2005
    #4
  5. Thank you for your input.

    I think my book is a bit Old. I bought it about 4 Years ago. I'll see
    about getting a new one. (-;

    Thanks again.

    Scott<-
     
    Scott Townsend, Mar 13, 2005
    #5
  6. Scott Townsend

    Paul Turvill Guest

    I'd say that the two holdowns surrounding the opening in the right-hand
    (east?) wall are redundant. Other than that the callouts are probably OK.
    The only one who can say for sure, however, is your local Building Official.
    ___
     
    Paul Turvill, Mar 14, 2005
    #6
  7. Thanks for the Input!

    I hopefully should be submitting the plans for a permit this week! Wish
    me luck!

    Thanks again!

    Scott<-
     
    Scott Townsend, Mar 14, 2005
    #7
  8. I work for a lumber company where our main focus is designing and
    fabricating trusses and wall panels. Within the last few months the issue of
    wall bracing has taken a few different paths as far as types and locations
    of bracing. The biggest change is the addition of engineered shear wall
    panels for the short walls to either side of the garage door and for walls
    over ten feet tall (this is all for residential BTW). We have been to almost
    every meeting put on by the local building officials (we are in Ohio) and
    also by Simpson Strongtie (they sell pre-fab shear panels) and what I can
    tell you is that each and every lecture we have been to has had a different
    way that they want to see things done.

    Our biggest problem to date is trying to educate the building inspectors on
    the correct ways to brace a wall line (according to the IRC).
     
    A guy named Joe, Mar 14, 2005